Basement insulation

MikeHazzard | Posted in Energy Efficiency and Durability on

Hi Everyone-

In the process of having my 1970’s basement renovated. Looks like it is simply batt insulation between 2×4’s with wood paneling, no drywall. I do not seem to have any moisture intrusion (no stains, mold/mildew smell) but will not know until the paneling comes down and the batt out.

What are my options for insulating this space? I do not want to take down the existing 2×4 frame.

Thoughts?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Mike,
    In most cases, the studs would need to be removed. Fortunately, that work is fairly easy to do and will happen quickly. In most cases, the studs can be reused.

    If there is a gap of at least 1 inch between the backs of the studs and the concrete wall, you could leave the studs in place -- but only if you insulated with closed-cell spray foam.

    If you plan to install rigid foam, the studs have to be removed.

    For more information, see How to Insulate a Basement Wall.