GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter X Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Plus Icon Minus Icon Picture icon Hamburger Icon Close Icon Sorted
Building Science

The Physics of Water in Porous Materials

Water has unique properties that govern its interaction with wood and other construction materials

Capillary action in concrete block occurs because water can defy gravity. The forces of attraction between water and hydrophilic materials allow it to climb to great heights.
Image Credit: Image #1: Building America Solution Center

I like to tell people I’m a recovering academic. The truth is, though, that I haven’t left physics behind. That would be impossible since I’ve been making a career in the world of building science. So today I’m going to delve into that subset of building science called building physics as we take a look at the physics of water in porous materials. You’ll also learn about the fourth state of water, the one that’s not liquid, not solid, and not vapor.

But fear not! I’m going to do all this with a lot of images, and I won’t include a single equation (although there’s a link to one if you’re brave enough to look).

The polar nature of the water molecule

Let’s begin with the water molecule. One oxygen, two hydrogens, bonded together covalently. That means each hydrogen shares its one electron with the oxygen atom and both atoms get to complete their outer shells by doing so.

[Image credit: Wikimedia Commons]
As it turns out, the oxygen atom pulls on that shared electron from each hydrogen atom more strongly than the hydrogens do, so the oxygen side of the molecule is slightly negative. The hydrogen ends are thus slightly positive. Because the water molecule is bent (as opposed to linear, with the hydrogens on opposite sides of the oxygen), the molecule is polar. It has a negative end and a positive end. The positive charge is concentrated in two areas near the hydrogen atoms, as you can see in the illustration at left.

[Image credit: Wikimedia Commons]
When you put a bunch of water molecules together, the polarity of the individual molecules causes them to attract each other. Like charges repel and unlike charges attract. As you see above, each water molecule can form weak bonds, called hydrogen bonds, with four other water molecules.

One consequence of water’s polarity is that it is a liquid at higher temperatures than similar molecules. Carbon dioxide, for example, is a linear, nonpolar molecule and becomes a gas at about -71° F (-57° C). If water were like carbon dioxide, the oceans would not be here. Mountains would have no snow. And I wouldn’t be writing this because we humans would not exist, at least not in the form we have now.

The polarity of water molecules means that when you put it in contact with another material, what happens depends on which attraction is stronger: water for itself or water for the other material.

When the water is more strongly attracted to itself, as you see on the left side of the diagram at left, we call the other material hydrophobic, or water fearing. When the water is more strongly attracted to the other material than to itself, we say that material is hydrophilic, or water-loving.

When the source is liquid water

Now it’s time to recall the Second Law of Thermodynamics: Water moves from wet to dry areas.

[Image credit: Stone Initiatives & Materials Testing Group]
If a porous material has one end sitting in water, the pores, or capillaries, will begin filling with water. The movement of water through capillaries depends on how hydrophilic, or wettable, a surface is and on how small the capillary is. The smaller the capillary, the higher the water can rise in it, as you see in the illustration at left.

The photo at the top of the article illustrates perfectly how water can move from the ground into the porous concrete and concrete block. It’s not uncommon for moisture problems in attics to originate with a wet foundation.

The photo of bricks below shows the capillary rise of water over time. After a bit more than an hour, the water is three-quarters of the way up the brick.

[Image credit: Wikimedia Commons]
How high can the water rise? I said at the beginning I was going to do this article without equations, so I’ll just tell you that there is one you can use to calculate the height a column of water can rise in a capillary. It depends directly on how wettable the surface is and inversely on the radius of the capillary, the density of the water, and the acceleration due to gravity. (If you want to see the equation, go to the Wikipedia page on capillary action and look for the section titled Height of a meniscus.)

Since trees move moisture from the ground to the leaves using capillary action, the photo below might give you an idea of how high water can rise.

[Image credit: Energy Vanguard]

(If you look closely, you might see me standing at the base of the tree. And if you do see me there, I’ll congratulate you on your imagination.)

When the source is water vapor

Liquid is easy. Things start getting fun when we take a look at what happens when water vapor interacts with porous materials. If you have such a material (drywall, wood, concrete, cellulose…) with humid air on one side, water vapor will find its way into the pores. If the material is hydrophilic, water vapor will start sticking to it.

And then we start using a new word. When the surface pulls water out of the air like this, we call it hygroscopic. The material is hygroscopic, and we also say that it has hygroscopic water on the surface.

[Image credit: Building Science Corporation]
Another word you need to know here is “adsorbed.” Those monolayers of water that stick to the surface are the fourth state of water. Here’s why.

When that first monolayer of water molecules begins sticking to the surface, it does so with gusto. Remember, we’re talking about hygroscopic materials that can pull water vapor from the surrounding space. They really like each other!

The second monolayer is also attracted strongly…but not as strongly as the first monolayer. Since the second monolayer is attracted to the surface through the monolayer of water that’s already there, the attraction is muted a bit. Likewise with the third, fourth, and fifth monolayers.

[Image credit: Building Science Corporation (with modification by Energy Vanguard)]
The diagram at left gives you a picture of that weakening attraction. The first monolayer is complete when the relative humidity rises to 10%. The relative humidity then has to rise to 50% before the second monolayer is complete. As the relative humidity keeps rising, the monolayers keep increasing and hit five by the time you get to 100%.

That attraction can be put in terms of energy. Recall that the energy absorbed or emitted when water boils or condenses is called the latent heat of vaporization. When water vapor adsorbs onto a surface (or breaks free of that adsorption), there’s a latent heat of adsorption involved.

According to Professor Chris Timusk, the heat of adsorption for the first monolayer is 3700 kJ/kg. For the second, it’s 2972 kJ/kg. At the fifth monolayer, the heat of adsorption is 2500 kJ/kg, which is equal to the heat of vaporization for liquid water.

What that means is that the adsorbed water really is different from the other three states. It’s obviously not vapor. It’s not ice either. It’s most similar to liquid water, but it’s not as free to move as liquid because it’s bound more strongly to the surface than it is to the surrounding water molecules. Only when you get more than five monolayers do you see it beginning to act like liquid water.

The three transport modes

Now we’re ready to talk about how water moves through porous materials. The three transport modes are:

  • Vapor diffusion
  • Surface diffusion
  • Capillary flow

Vapor diffusion carries water vapor through the material in the vapor state. It doesn’t stick to any of the surfaces it encounters. It just floats on through in the empty space of the pores. Not much water gets through like that.

Surface diffusion moves more water than vapor diffusion. This happens because of that attraction I discussed earlier. Since the first monolayer is attracted the most strongly, it’s energetically favorable for a molecule in the second monolayer to move down to the first layer if it can, as shown below.

[Image credit: Building Science Corporation (with modification by Energy Vanguard)]
Likewise, molecules from the third monolayer want to move down to the second, the fourth to the third, and so on. In that fashion, water can move through a porous material via surface diffusion.

But things really open up when the capillaries start filling up. Once a pore is completely full, water can move more rapidly through the porous material. That’s capillary flow.

Sorption isotherms

Now we can put all this together and understand what’s going on in these geeky things called sorption isotherms. The graph below, taken from Professor Timusk’s doctoral thesis, is a good example.

[Image credit: Professor Chris Timusk]
First, let me point out that there are three curves here: two for different densities of wood and one for clay brick. Each one shows the moisture content in the material as a function of the relative humidity of the surrounding air.

Notice that each curve exhibits the same pattern: a rapid rise, a flattening out, and then another rapid rise. Recalling the explanations above for adsorption and the three types of moisture transport, what do you think is happening in those regions? See if you can figure it out before going on to the next paragraph.

[Image credit: Graham van der Wielen on Flickr.com]
To distract your cheating eyes from “accidentally” reading the answer first, I’ll let you look at this picture of aliens drinking beer. Now think!

Well, first off, the curves show surface diffusion and capillary flow. We know capillary flow starts at higher relative humidities, so the initial rise and the flattened out part are where surface diffusion is happening. But why does the initial rise flatten out so quickly?

Recall that the first monolayer feels the strongest attraction for the surface. It gets filled at about 10% relative humidity. The flat part of the curve is mostly filling the second monolayer plus a bit more in wood and significantly more in brick.

When the curves shoot up again, capillary flow has kicked in (see graph below). Now the moisture content can increase rapidly with increasing relative humidity. And here’s where we can see something really interesting about the difference between materials.

[Image credit: Professor Chris Timusk]
Notice that capillary flow doesn’t start in the brick until the relative humidity is much higher than in the two types of wood. Hmmm. What could cause the capillaries not to fill up at lower relative humidity like it does in wood? Why of course. It’s because they’re bigger!

Another important thing to know about sorption isotherms is that the curves you see above are for a specific temperature. As you raise or lower the temperature, the curves shift. Why? Because the amount of moisture a material can hold at a give relative humidity depends on how warm or cool it is.

Warmer materials cannot hold as much moisture because there’s enough heat there to dry them out. Cooler materials hold more moisture.  In fact, Bill Rose calls this the Fundamental Rule of Material Wetness: Warm materials tend to be dryer and cool materials tend to be wetter.

And now you can look at sorption isotherms and understand what they’re telling you about materials… without being a scientist or academic, practicing or in recovery.

Sources

The main source I used for this article was chapter 3 of Professor Chris Timusk’s doctoral thesis (pdf). Most of the rest came from Dr. Joseph Lstiburek’s presentations on building science fundamentals and hygrothermal analysis, Wikipedia, and Bill Rose’s book, Water in Buildings.

Allison Bailes of Decatur, Georgia, is a speaker, writer, energy consultant, RESNET-certified trainer, and the author of the Energy Vanguard Blog. Check out his in-depth course, Mastering Building Science at Heatspring Learning Institute, and follow him on Twitter at @EnergyVanguard.

4 Comments

  1. user-4739854 | | #1

    Thank you!
    Dr. B,

    That was wonderful. Now some questions... does the capillary flow of concrete increase as the MPa increases? Is there a relationship?

    What about Critical Degree of Saturation (Scrit) in concrete: is there a relationship to MPa?

    Finally, were the aliens in question using capillary flow or good old fashioned depressurisation to pull up the beer?

    Thanks for digging into this, now I can sleep at night.

  2. user-741168 | | #2

    trees?
    There's a problem with using tree sap in explaining capillary flow. The capillaries in building materials all have a meniscus (They have menisci?), or an interface between liquid and vapor. There's no meniscus in a tree. An old guy complimented me once on a tight woodworking joint saying "Looked like it growed that way." Same explanation for water filling the xylem cores. Growed that way.

  3. GBA Editor
    Martin Holladay | | #3

    More on sap
    Allison and Bill,
    Back in January 2004, I wrote an article on capillarity, noting, "Contrary to popular belief, capillarity is not responsible for the rise of maple sap from underground roots into sap buckets."

    A Cornell University web site provides more information on this topic:

    "What causes the sap of maple trees to flow in the spring? During warm periods when temperatures rise above freezing, pressure (also called positive pressure) develops in the tree. This pressure causes the sap to flow out of the tree through a wound or tap hole. During cooler periods when temperatures fall below freezing, suction (also called negative pressure) develops, drawing water into the tree through the roots. This replenishes the sap in the tree, allowing it to flow again during the next warm period. Although sap generally flows during the day when temperatures are warm, it has been known to flow at night if temperatures remain above freezing.

    "Thus, pressure and suction are essential to sap flow. But how do the pressure and suction develop?

    "Sap flows through a portion of the outer tree trunk called sapwood. Sapwood consists of actively growing cells that conduct water and nutrients (sap) from the roots to the branches of the tree. During the day, activity in the cells of sapwood produces carbon dioxide. This carbon dioxide is released to the intercellular spaces in the sapwood. In addition, carbon dioxide in sap is released into the spaces between the cells. Both of these sources of carbon dioxide cause pressure to build up in the cells. A third source of pressure is called osmotic pressure, which is caused by the presence of sugar and other substances dissolved in the sap. When the tree is wounded, as when it is tapped by a maple producer, the pressure forces the sap out of the tree.

    "At night or during other times when temperatures go below freezing, the carbon dioxide cools and therefore contracts. Some of the carbon dioxide also becomes dissolved in the cooled sap. Finally, some of the sap freezes. All three of these factors create suction in the tree. This causes water from the soil to be drawn up into the roots and travel up through the sapwood. When temperatures rise above freezing the next day, sap flow begins again."

  4. ronaldsauve | | #4

    Solids vs. air
    It is interesting to me too, that while solids hold more water when cool, that with air, it's just the opposite. Warmer air holds more moisture than cool air. Interesting world we live in.