XPS vs EPS — Below-grade slab insulation
![](https://secure.gravatar.com/avatar/5730210db14ba879cf3601ecc4361563?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fp.png&r=g)
Home Depot now sells pink XPS from Owens Corning. A 10 foot sheet by 2 feet wide was only $10 per sheet. The R-Value was R-5 per inch of foam.
I like the way XPS is easy to score and break without having EPS snow everywhere. The XPS also carries a higher R-Value per inch.
Which is better to use below grade under a slab? Which can carry the higher concrete loads of a slab?
Both are fine. Buy recycled.
The R5/inch eventually drops to R4.2/inch for 1.5lb density XPS (Foamular 150), as it's HFC blowing agents leak out to do their climate damage. At 20 years it can't be counted on for even R4.5/inch despite the "lifetime warranty" of always retaining at least 90% of the labeled R. (It's a warranty that would rarely be taken, since the cost of sampling and re-testing, and the cost of re-installing would make collecting on it prohibitive.)
At 1.5lbs density "Type-II" EPS, is also R4.2, and does not rely on blowing agents for it's performance- it 's performance on day 20,000 will be pretty much what is was on day 1.
Cost-wise Type-II EPS is typically 20-25% cheaper per labeled R than XPS (and it's a stable R over time.)
XPS has a somewhat higher compression rating than EPS, but they are both several times higher than necessary for supporting a slab. (But neither are good enough for going under a footing that is supporting the whole house unless the footing has been engineered for it.)
Type-I EPS (1lb per cubic foot nominal density) is fine for below grade walls, but can take on enough moisture under slabs to take a performance hit under super-wet conditions. It's usually labeled ~R3.9/inch.
Cutting EPS with a heated 4" putty knife with (with the side sharpened) makes quick work of up to 1.5" material (R6-ish). Some people rig up heated wire for doing artsy-craftsy complex shape cutting of polystyrene, but for straight cuts heating a putty knife blade works fine.
Peter,
Stephen and Dana gave you good advice. For more information, see this article: Choosing Rigid Foam.