XPS foam board on the interior side of kraft-faced fiberglass
![](https://secure.gravatar.com/avatar/01f73ccb3664fd3e97de891b83fe9a24?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fb.png&r=g)
I live in southern Maine, zone 6 and I have a 95 year old bungalow that we just built a 12 x12 dormer on. The plan was to use cathedral r30 unfaced fiberglass followed by 1/2 inch XPS and then strapping and drywall.
I came home to my builder using faced r30 (which was put on AFTER he strapped the ceiling) and running the xps in strips in between the strapping…
Obviously a miscommunication. My question is, will the two vapor retarders cause problems?
Thanks,
Bob
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
Bobby,
No, these two adjacent vapor retarders won't cause any problems.
The main problem with this roof assembly is its low R-value. In your climate zone, you should really be aiming for R-49. Most of the R-value of your roof assembly comes from the R-30 fiberglass, and the performance of that insulation is reduced by thermal bridging through the rafters. And 1/2-inch rigid foam has a very low R-value -- about R-2.5. Finally, the performance of the rigid foam has been greatly compromised by cutting it into thin strips and inserting it between the strapping.
Unless it has vapor retardent facers1/2" XPS isn't even a Class-II vapor retarder- it's only slightly more vapor tight than latex ceiling paint.
If the R30 has a foil facer (unlikely) that would be a Class-I vapor retarder, limiting what you can do later. If it's a kraft facer, it's a "smart" vapor retarder, usually about 0.5 perms when dry, but 5 perms or higher when the humidity in the fiberglass is high.