Window & door header insulation options – Zone 5
2×6 stud walls, and the header’s have an inside and outside vertical 2×8, with the 2.5” center is empty. The outside sheathing is 1” polyiso with a foil (no OSB or plywood). I want to fill the headers before the windows are installed this week. Drying is to the inside, so no inside VB, and permeability is important. I was thinking 1.5” R6 Roxul ComfortBoard IS or 2” R8 EPS foam. I tried window/door spray foam, but the 2.5” gap was too large, and the foam just falls out to the floor. Am I overthinking this, and I can just stuff it with pink fiberglass?
Thanks,
J
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Jeff,
Buy some rigid foam insulation with a total thickness of 2.5 inches (for example, 1.5 inch + 1 inch). The rigid foam will do a better job than fiberglass.
I found some 2.5" R10 EPS foam tonight. They're installing the windows tomorrow, so I was able to cut it and get it installed tonight. It worked perfect, with a nice tight fit.
Thanks Martin, your advice is always appreciated.
Jeff