Will this keep moisture off my fiberglass batts?
![](https://secure.gravatar.com/avatar/bdf4cee3b9259affaf357873c86ba644?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fn.png&r=g)
Neilc1
Will this 1″ XPS board keep moisture off my fiberglass batts in the stud bays in my basement?
Should be more informative,I got enough of this 1" Xps roofing board for free and have put it up against all my poured concrete walls,now I am ready to stud the walls and then Sheetrock,I know it's not the best but the price was right and I talked with Owens Corning and they feel I should be ok with it but wanted a other opinion,I actually got enough to double it up on some walls to make 2",so minimal 1" plus 4" of batting should give me a descent r value
Neil,
I think you forgot to tell us your location or climate zone.
Massachusetts zone 5 I believe
Tape the seams and can-foam the edges, and yes, R5 XPS is sufficient for dew point control on the above-grade portion for up to 2x4/R15 without interior vapor retarders in zone 5. The ~1-1.5 perm vapor retardency is a sufficient vapor retarder against ground moisture for the below grade portion, assuming it's a reasonably dry foundation wall (no history of bulk water leakage of that wall.)
And, 1" XPS + 2x4/R13 would meet the IRC code-min performance equivalent to R10 continuous insulation for basements in zone 5.
http://publicecodes.cyberregs.com/icod/irc/2012/icod_irc_2012_11_sec002.htm
In MA there are multiple vendors of reclaimed roofing foam. It may be cheaper to go with 2-2.5" everywhere than to use batts in the studwalls. Nationwide Foam in Framingham and Green Insulation Group in Worcester are probably the biggest, but there are others.