Will 1/4″ thick Pactiv fanfold foam work as a vent baffle in combination with mineral wool?
![](https://secure.gravatar.com/avatar/c4e9dda17d4c647e6076764038232616?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
designc
Sorry the previous question got cut off.
I’m not sure whether it’s a condensation problem, as thin as it is.
Fanfold is thin, but it usually comes with thin polyolefin facers that brings it's vapor permeance down to 0.6-2.0 perms (1 perm or less would be class-II vapor retarder.) Unfaced half-inch XPS would run about 2-2.5 perms, 1" unfaced type-I EPS would be about 5 perms, nearly an order of magnitude higher drying rate than fan-fold with facers.
Look up the specs for the specific products you have in mind. Some fan-fold perforated on a 1-2" grid to make it highly permeable. The Pactiv fan-fold goods in this spec sheet all have a vapor permeance no greater than 1.7 perms:
http://www.ujr.ca/EN/PDF_Support_Files/insulation/greenguard/xps/greenguard-fanfold-siding-underlayment-data-sheet.pdf
That's a bit on the tight to put on the exterior of a batt- ideally you have an equal or lower permeance vapor retarder on the interior side of your rock wool. But it's not terrible- the assembly can still dry into the ventilation gap. Your climate and the construction of the rest of the assembly make a difference.
Thank you D, I do plan to add a min.1-1/2" polyisocyanurate to bottom of rafters.
Also, I'm not sure which exact Fanfold is sold by Lowes. But that is the product in question.
It looks like a fairly easy way to get a seamless baffle on the cheap.