When installing retrofit windows, what type of insulation works best overall? Fiberglass, open cell foam tape, or spray foam?
![](https://secure.gravatar.com/avatar/918c91dec3d3e0bff3a693c390d3b417?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fb.png&r=g)
When installing retrofit windows, what type of insulation works best for overall performance? Fiberglass, open cell foam tape, or closed cell spray foam?
Bradley,
Retrofit window installation does not usually require any insulation improvements to a home.
Perhaps you are asking about air sealing the gap between the new window frames and the rough opening?
Brad
I figured you meant the gap between the window frame and the rough opening. Use a minimal expansion foam specifically for window installation so you don't warp the window frame and cause operation problems. There are a ton of manufacturers. I personally use Todol products that I get from EFI. Fiberglass insulation is not an air barrier and a waste of time and effort. More than likely the old gaps were filled with pieces of batts. They are usually covered in black, which is a sign of air infiltration. I have never used open cell foam tape (unless you are referring to weatherstripping) I personally would not use that either because the adhesives on the tape fail over time.
My trick, I oversize rough opening which gives me more room to fit low expanding spray foam in deep. I just seal the deep area, then add fiberglass to fill out area. The fiberglass stops the foam from frothing out and then needing to be removed.