Hi
I wanted a opinion on if ventilation baffles area needed in my situation.
The house has a covered porch and the vented soffit will be 7′ out from the house wall, there is then a 2′ high OSB above the top plate to keep the insulation in, with 15″ opening above it. It’s then 20’+ to the ridge vent.
1st picture looking from wall out to soffit opening
2nd picture distance between soffit and wall
3rd picture looking at wall up to rigid vent
Thanks for any help
Dave
Zone 6
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Dave, there is no need for insulation baffles in your situation.
Just to be clear: this is a vented attic with the air control layer at the floor of the attic/ceiling of the top floor.
Peter
Thanks Michael
Peter,
you are correct, unconditioned attic with air control layer at celling/ attic floor.