Vapor barrier with mineral wool insulation
![](https://secure.gravatar.com/avatar/89e83c93b5743955697bc5fef66bd947?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fp.png&r=g)
I am building a garage apartment home in southern Vt zone 6. I have caulked (from the inside) everywhere that I think air may come in from the outside. I am using r23 rock wool 5 1/2 batt insulation. Should I put up a vapor barrier over the rock wool?
https://www.greenbuildingadvisor.com/article/do-i-need-a-vapor-retarder
In zone 6 you'd still want a Class-II or tighter vapor retarder on the interior side of walls, independent of sheathing & siding type. Air tight drywall with vapor barrier latex primer is safer/better than 6 mil polyethyene, and a "smart" vapor retarder such as Intello Plu$ or Certainteed MemBrain is a bit safer than vapor barrier latex.
But the most important thing is air tightness to the conditioned space/interior, and fitting the batts carefully to prevent easy convection inside the cavity.
It's OK but not necessary in zone 6 to install vapor barriers for VENTED roofs. But unvented roofs are a whole other topic.
This is a case where testing is better than thinking.
That is correct jon everywhere that I think air may come in. like cracks and crevices and places where you can see lite coming through. That's a good test. If light shines through then air will come in through that same spot.
Light only travels in straight lines- air can follow very convoluted paths. The daylight test is only going to catch a tiny fraction of the air leaks.