Vapor barrier or not?
I’m building a heated workshop in SE Michigan – Climate zone 5. Insulated slab with 6 mil vapor barrier. I’ll be using a Reznor sealed combustion unit heater- 83% efficent. This is my wall assembly: 5/8″ T1-11 plywood siding, 3 coats of acrylic paint, Tyvek, 2×6 studs and rockwool insulation. I plan on using the Air Tight drywall method. Do I need a vapor retarder? If so would vapor barrier paint do the trick?
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Make sure that the wall complies with the recommendations in Table 2 A or B here. Always air seal it well and test to verify.
Hi Jon,
Where is the Table you refered to? There wasn't a link in your reply.
Marty
Click on the word "here" in response #1.