Vapor barrier

garyov | Posted in Green Products and Materials on

I have read that with me putting two layers of 1 1/2 inch foil-faced rigid foam with staggered joints on the outside walls, I don’t put a vapor barrier on the inside.

Now on my low-slope roof, I have 2×12 rafters. Starting at the top, I have:

Shingles-
15 lb. felt paper-
ice shield over the full roof-
1/2 inch plywood sheathing-
1 5/8 inch air space to vent-
1 inch foil-faced rigid foam, caulked at the edges-
1 1/2 inch foil-faced rigid foam, caulked, with staggered joints-
2 inch foil-faced rigid foam, caulked, with staggered joints-
5 1/2 inch Roxul insulation.

Do I put the vapor barrier on the inside?
Thank you.
Gary

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Gary,
    The short answer is no -- you don't want to install a vapor barrier on the interior of this assembly.

    The justification for interior vapor barriers -- a justification which has little scientific basis -- is that an interior vapor barrier keeps sheathing dry by preventing outward vapor diffusion during the winter. In the type of roof assembly you are describing, the exterior rigid foam keeps the sheathing warm and dry all winter long. (If the sheathing is warm, condensation and moisture accumulation are impossible.) So you don't need interior polyethylene.

    (Interior polyethylene can cause problems during the summer, since the polyethylene prevents the roof assembly from drying toward the interior.)

    Your roof assembly has a total R-value of about R-47 -- perhaps a little less -- with about 57% of the R-value provided by the exterior rigid foam. That is a robust roof assembly for all climate zones except Zone 8, so you should be fine unless you live in a very cold location.

    For more information on this type of roof assembly, see How to Install Rigid Foam On Top of Roof Sheathing.

    Two more points:

    1. I assume that your stack-up includes a layer of plywood or OSB roof sheathing between the bottom layer of rigid foam and the 2x12 rafters. Is that correct?

    2. When you install the Roxul mineral wool in the rafter bays, remember that the mineral wool batts have to be in direct contact with the roof sheathing. One way to do this is with steel wires designed for the purpose.

  2. garyov | | #2

    martin i,m not sure you under stand my assembly but the rigid foam is under neath the 1/2 inch sheathing.I have 1 5/8 vented air space then the rigid foam in the rafter bays and then the batts tight agianst the foam

  3. user-2310254 | | #3

    Gary:

    Where are you located.

  4. Expert Member
    Dana Dorsett | | #4

    The vented air space doesn't affect Martin's answer. The vent space provides a path for the roof deck to dry, and to purge any minor air leaks in your cut'n'cobbled foam. A vapor barrier on the interior isn't necessary to keep the fiber dry- the foam-R/fiber -ratio is sufficient to keep wintertime moisture accumulation to acceptable levels.

    Adding a vapor barrier on the interior would prevent the fiber insulation from drying, reducing rather than enhancing the resilience of the assembly,

  5. garyov | | #5

    i am in northern michigan

  6. GBA Editor
    Martin Holladay | | #6

    Gary,
    I guess I did misunderstand. I assumed that the rigid foam layers were continuous layers that covered the entire roof. Instead, it sounds like you cut the rigid foam into narrow rectangles and inserted the narrow rectangles between the rafters (the cut-and-cobble approach).

    Installing the rigid foam in continuous layers would have been much better. If you are still at the design stage -- if you haven't built this roof yet -- you might reconsider your plan.

    If the roof assembly is already built and insulated, it will work -- even though you'll have thermal bridging through the rafters.

    As Dana Dorsett noted, my answer on the polyethylene is unchanged.