Unfinished Basement Insulation Requirements – IECC 2009
![](https://secure.gravatar.com/avatar/565191afbc55e1d109a275737ddd39f6?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fd.png&r=g)
Hello All,
I recently just purchased a new home. When I signed the contract, the local residential building code was to use the IECC 2009 requirements. I built in zone 5.
As far as I can tell, it explicitly says that basement walls should be insulated.
The builder insulated one wall cavity (approximately 12′ x 4′) and thats it. The entire basement has concrete walls. Additionally, they did not insulate the ceiling, or the walls against the staircase which I think they are required to do if they did not insulate the basement?
I am using 2x more natural gas then average in my area for a brand new home. Something does not seem right. I am very obviously a layman so I don’t want to try and fight the builder to do more insulation without some ammo. I would appreciate any advice. Thanks!
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
2009 IECC Table 402.1.1 Insulation requirements for basement walls in CZ5 are R10 continuous insulation or R13 cavity insulation. I would make sure your sill plate, rim joist and any opening thru the walls are well sealed and insulated as well. Insulating the ceiling will work if there is a door between floors.