Understanding blower door numbers. Air seal to 62.5 cfm 50
I’m trying to understand a number that I was given by mass save. I convinced them to reconsider air sealing and they’ve agreed. They’ve proposed to air-seal to “62.5 cfm50.” How do I convert that to ach50? I had a blower door test done already which found “20,980 cubic ft.; 2600 cu ft/min = 156,000 cu ft/hr. hence 7.4 air changes/hour.” which included our basement. 5.7 ach50 with basement door closed. Zone 5, outside of Boston, 1915, 1.5 level bungalow, 1620sqft which does not include the basement.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
You've got the formula right there. 62.5*60/20980= 0.18 ACH50.
Thank you. I didn’t think this was correct though. Mass Save is not air sealing to less passive house standards.
Maybe they've got an errant decimal point.
I suspect they meant 62.5 cfm ACHnat. Which is around 3 ACH50.
Jon, I believe that makes the most sense. Not a decimal error because I’ve seen others with similar quotes. Thanks!