Under-floor hot water coils
I have a hot water underfloor (pex tubing) loosely run in between the joists (as if you uncoiled a new hose) & not close to floor with a foam board attached at btm of joists. It is very slow to reach set points & will over ride up to 2-3 degrees. I was considering attaching the metal plates with the tubes touching the floor but labour intensive with 3 ft crawl space & folks say it will be noisy. Friend suggested to remove u clips that hold the coils & use bubble back insulation to push coils close to floor & then add more insulation Roxall R 20 to bottom & then finish off with the foam board. Any suggestions? Need Help please.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Peter,
Here is a link to a GBA article that discusses this issue: Lessons Learned the Hard Way. The author, Ed Welch, agrees with you: heat transfer plates are a good idea.
If you can't stomach the work associated with installing heat transfer plates, you could try raising the temperature of the water -- but be careful, because higher temperatures can damage some types of flooring, be uncomfortable, and raise your energy costs -- and/or increasing the amount of insulation under your joist bays. Forget the bubble wrap -- use rigid foam, and seal the seams.