Trying to make sense of IRC2021 roof insulation requirements
![](https://secure.gravatar.com/avatar/f2b7adba225fa7cdc3c8d3f0c721f906?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fa.png&r=g)
I’m hoping my friends and colleagues here can help me make sense of the IRC2021 roof insulation requirements.
“Assemblies shall have a U-value equal to or less than that specified in Table N1102.1.2…”
Table N1102.1.2 gives U values for roofs. For example zone 6 = 0.024
The next paragraph says, “Assemblies with an R-value of insulation equal to or greater than that specified in Table N1102.1.3 shall be an alternative to the U-factor in Table N1102.1.2”
For zone 6 Table N1102.1.3 an R-value = 60.
As I read this I should be able to use either table.
By definition R-value = 1/U-value
If I go with the U-value table I need a U-value no greater than 0.024. This translates to an R-value = 1/0.024 = 42
So according to the U-value table I can meet the requirement with R42 insulation but according to the R-value table I need R60. That’s a big difference.
I understand that the U-value is referring to the entire roof section, including thermal bridging at trusses and rafters. But if, for example, I do R25 of continuous rigid insulation above the roof deck and r21 high density batt insulation between the top chord of my roof trusses I can easily meet the R42 criteria. Does that mean I don’t have to go to R60?
Yes. If you use a hybrid system and the calculated whole-roof U value is less than .024 you are OK. The R-60 requirement is for the insulation only, when using cavity insulation with no continuous insulation.
Thanks!
I just did the math and it looks like I can make it work with 4.5" of rigid insulation on the roof deck and R21 batts underneath. It satisfies the condensation control provisions of IRC 2021 as well.