Tape Sheating Seams or Detail WRB as Air Barrier
JayMart | Posted in Energy Efficiency and Durability on
Hi GBA Community,
New build in Zone 5 and I’m trying to figure out my Air Barrier situation and needed some advice.
To set some context, standard timber construction – Exterior 2x6s – Single Bottom Plate and Double Top Plates – 1/2″ Plywood Sheathing – Plan is for a Brick Skirt and Vinyl siding
First Question: If I go with Siga Fentrium & Wigluv for the foundation and sheathing connection and the seams respectfully, is going with the Majvest 200 on top of that overkill?
Another factor is that my project will be sitting over the winter with no siding so I’m nervous about the UV exposure. The Siga rep has said that as long as I don’t go over 9 months I should be okay (the Majvest 200 product data sheet says 3 months). My other option is Tyvek CommercialWrap as that is rated for 9 months exposure.
(Majvest is $0.24 a sq/ft and CommericalWrap $0.27 sq/ft)
Should I skip the taping on the seams to save time and try to detail with WRB to serve as my air barrier? I’d be doing the work myself so I need something that is easier and most effective.
Should I chance the Siga Majvest over the Winter? Or, go with the Tyvek?
Any advice would be greatly appreciated.
Thanks,
Jason
  1. Patrick_OSullivan | | #1
    I wouldn't try to detail a traditional WRB as an air barrier. One wrong move and your efforts to make it an air barrier are now causing it to trap water against your sheathing.
    You can tape your sheathing seams as mentioned and then just detail the WRB as a WRB. Or, you could investigate self adhered WRBs which will solve both problems. If I were doing the work myself, I would probably opt for a self adhered WRB.
    1. finePNW | | #5
      “One wrong move and your efforts to make it an air barrier are now causing it to trap water against your sheathing.”
      If you happen to recall, what types of wrong moves could lead to this? Thanks!
      1. Malcolm_Taylor | | #7
        finePNW,
        A horizontal run of tape that doesn't fully adhere can channel and retain water behind it. If the WRB doesn't have to be air-sealed, it can just rely on laps.
  2. finePNW | | #2
    I know I’m a bit late here, but I’m considering a taped WRB as air barrier, and curious what sort of pitfalls should be looked out for— or why I should maybe opt for taping sheathing instead. Most of my walls are plywood sheathing but some are old shiplap with *lots* of seams that would need taping.
    1. Patrick_OSullivan | | #3
      Think of taping a WRB as an air barrier as if you were asked to construct a balloon out of scraps of paper. It's doable, but a lot can go wrong.
      With panel sheathing, taping seams is a no-brainer. Any areas with board sheathing, I would switch to a self-adhered WRB such as Henry Blueskin. You can easily transition between the two and get the best of both worlds.
      1. finePNW | | #4
        I’ll look into that. Thanks!
    Akos | | #6
    Taping the WRB for air barrier is hard to get right as the WRB can balloon under positive pressure and you can get a lot of 3d air flow paths. Sheet WRB can also get damaged during a build which generally won't create water issues but can reduce air sealing.
    Neither of these can happen with taped sheathing, that is why it works. It is simple and extremely effective.
    You also have the bonus of the tape being protected by the WRB so in case of longer than expected UV exposure the tape won't get damaged.