Tape House Wrap or Exterior Foam
user-7653783 | Posted in General Questions on
I’m planning to install new vinyl siding on my house with 1” xps foam insulation in climate zone 5 with 2×4 walls. The build up will be plywood, house wrap, 1”foam, and vinyl siding (with no air gap).
in this situation, should my air barrier be foam with taped seams or house wrap with taped seams?
greg
    BILL WICHERS | | #1
    It doesn't hurt to do both for some extra insurance. I would use polyiso though instead of XPS, which is a bit better for whole-year averaged R value, will be much easier to tape well (most tape doesn't like to stick to XPS), and will be greener too.
    1. user-7653783 | | #2
      Thanks for the reply. Could taping both lead to issues with trapping water? If I could only tape 1 which would be better?
    Akos | | #3
    For a solid air barrier, you want to tape the sheathing. This generally gets you the best air sealing for the least amount of work.
    Make sure you seal up the sheathing to foundation transition as this is a big leak in most houses. Liquid applied sealant or a tape specifically rated for concrete is the best for this.
    If you can get at it, taping from the sheathing across your wall top plate and onto the ceiling drywall would seal next biggest leak spot.
    Once your sheathing is sealed up, taping the rest of the layers is optional. About the only thing I tape after the sheathing is any vertical seams in house wrap.
    1. Malcolm_Taylor | | #4
      Akos,
      I might be wrong, but I think this is a re-siding of an existing house, so the sheathing might have quite few holes in it. My preference would be a fully adhered WRB, if not that then a sealed regular WRB, and the foam as the option I'd least like to use.
      If this is a new build, then definitely the sheathing.
      1. user-7653783 | | #5
        Thanks. Yes the sheathing is a mix of plywood and old boards so I don’t think taping the sheathing is an option because the boards are relatively narrow
  3. user-7653783 | | #6
    1. Malcolm_Taylor | | #7
      User ...783,
      They are using the foam as a WRB.