Subfloor insulation material?
![](https://secure.gravatar.com/avatar/f8e1eb3897932c7135b58ca31aec9808?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fr.png&r=g)
I am building a new house and plan to use Green Fiber cellulose for wall (dense packed) and attic floor (loose) insulation. I was told that cellulose does not work for subfloor insulation. We have raised foundation with 2′ vented crawl space in California.
I don’t mind using fiberglass in closed cavity walls and plan to use it for interior walls for sound barrier. However, I prefer not to use fiberglass for subfloor insulation. Is there any other alternative?
Rian,
Some crawl spaces are damp. For that reason, I suggest that you install rigid polyisocyanurate insulation on the underside of your floor joists. Do a good job of air-sealing the polyiso seams, as well as the perimeter of the insulation.
If you feel confident that your crawl space will be dry, you could install dense-packed cellulose in the joist bays above the polyiso. However, since most floor joists include plumbing pipes (with their periodic leaks), there is a certain logic to skipping the cellulose and sticking with polyiso.