Steel frame steel building home/ condensation issues
Have a steel framed steel building house. Standing seam metal roof with cathedral t&g carsiding. I am having condensation issues. 2x4s attached to bottom of steel purlins running from ridge to eave on bottom side. 10” of insulation between purlins. Condensation only happens after cold night 25 degrees or less, and then warms up next day.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
https://www.buildingscience.com/documents/insights/bsi-036-complex-three-dimensional-air-flow-networks
You need an air barrier on the interior side of the assembly. T&G carsiding isn't up to the task. The steel purlins are thermal bridges; they will nearly always cause condensation unless the are insulated on the exterior.