Siding failure issue, climate zone 5B / 6B, north central Colorado.
![](https://secure.gravatar.com/avatar/8950d23c3af5cd82008e53e5b31f7818?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fj.png&r=g)
22 year old home, T1-11 wood siding failing (cupping, delaminating, peeling away). T1-11 is siding over 1/2″ blueboard over 2 X 4 framing (16″ o.c.), with blown-in cellulose insulation, 1/2″ sheetrock inside. Can I cut out damaged sections of siding, patch back in with OSB or 1 by roughsawn, then 15# roofing felt, then corrugated metal low and traditional stucco above? Dry, windy climate, intense sun, low interior humidity, limited budget. Any thoughts / suggestions? Thanks in advance.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
It sounds like a good plan. You're using the repaired T-111 as the sheathing, and adding a good rainscreen. Just make sure the T-111 is at least 6" above grade everywhere, and install a z-flashing strip at the stucco/metal joint that will kick out any water running behind the stucco.
Joe,
I assume that the T-111 is about 5/8 inch thick. If I'm right, you can't patch the damaged T-111 with 1-inch rough-sawn boards. You have to patch it with 5/8-inch exterior plywood or more T-111.
If you want your wall to perform well, you want to pay attention to airtightness when making your repairs. If possible, seal all seams between the T-111 panels and the repaired areas with a high quality tape like Siga Wigluv.
I understand that you have a limited budget, but you should still know that stucco can be a tricky cladding to install. For more information on potential stucco problems, see To Install Stucco Right, Include an Air Gap.