Roof venting question

knobhead | Posted in Green Building Techniques on

Martin:
I live in Zone 5 and anticipate building soon. I got a building permit in Dec. 2009 before the new code was enacted.

My architect and I submitted plans for a 1,700 sq. ft. footprint, with the basic, called for insulation to code in the drawings. And now we hope to show 4″ rigid on the walls and I thought 2″ rigid on the roof sheathing, and possibly R-30 or R-38 tacked between the rafters or trusses would do.

But the architect is not sure it will meet code, because the walls are 26′ apart and either system would most likely require collar ties, in which case there would be SPACE between the batts and the roof/rigid, and it would need to be vented to code, correct?

This kind of goes against my tight envelope plans……He suggested I check with you. What are we missing here, Martin?
Steve B.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Steven,
    I'm not sure I understand your question correctly, but I'll take a stab at interpreting it. I think you are asking whether it makes sense to have ventilation chutes under the roof sheathing, fiberglass batts between the rafters, and rigid foam above the sheathing.

    If that's your question, the answer is no. If you install ventilation chutes between fiberglass batts and the roof sheathing, it makes no sense to install rigid foam on top of the roof sheathing.

    If I guessed wrong about your question, please rephrase your question.

  2. knobhead | | #2

    Martin:
    Really sorry this is not coming out right. My initial plan was build envelope utilizing rigid only on advantech sheathed roof, but leery using 6+ inches rigid(fastening). Apparent need to compromise with NYS code and of course independent township enforcement. What insulation system can I use on roof to get me cathedral or modified cathedral, and for that matter, the rest of house with flat ceilings, using EITHER 2X lumber or trusses?? The plan is r-26 rigid walls (2x4 walls to keep window box out to minimum). Shooting for Huber zipped walls, and hoping to get minimum air changes, and using fan only (Braun) ventilation. Is there a simple roof insul. system that will agree with town/state and my energy anticipations?

  3. GBA Editor
    Martin Holladay | | #3

    Steven,
    That's a very broad question, and of course there are a huge number of answers. For an insulated sloped (cathedral) ceiling, you can use any of the following:
    1. Thick foam above the roof sheathing.
    2. SIPs
    3. Nailbase on top of roof sheathing.
    4. A combination of foam above the roof sheathing and cavity insulation in a hot (unvented) roof.
    5. Spray foam insulation between the rafters.
    6. Dense-packed cellulose under a ventilation chute.

    ...and that's just a sampling. There are lots of ways to build!

    For an insulated flat ceiling, you can use:
    1. Thick cellulose
    2. Thick blown-in fiberglass
    3. Spray-foam insulation

    ...and many other types of insulation.

    Can you narrow your question?

  4. knobhead | | #4

    Boy! Let me try to better explain.....Whether i use rafters with a collar tie,OR trusses with a bottom plate that is lower that collar tie, I still have an air space somewhere with un-conditioned space that architect says needs to be vented to code. I'm thinking that whatever insulation system used,IF it is applied ABOVE air space, such as rigid on sheathing, with possible 1-2" flash under sheathing, then I would be fine, code wise, to not require venting,which I DO NOT WANT!!I realize there is some heat loss from below modified cathedral, thru drywall, to un-cond. space, but with a hopeful 1-2 Ach/hr home, I should be good. Does this game plan meet with building code specs in your opinion?

  5. user-869687 | | #5

    Steven,

    I think your architect is correct that if there is an unvented assembly with rigid insulation above the sheathing, then there should not be any air space between the underside of sheathing and any additional cavity insulation. If you don't think it's possible to install cavity insulation without this undesired air space, then your alternatives would be either (1) rigid insulation only, thicker with long fasteners as you say, or (2) cavity insulation only, with venting as required by code.

    With the latter you would want to pay special attention to air sealing the drywall at the ceiling, to meet your goals for air tightness. Avoid can lights and seal all penetrations carefully before installing the insulation.

  6. GBA Editor
    Martin Holladay | | #6

    Steven,
    Your writing is unclear, and I have no idea what you are talking about. Let's start at the beginning.

    1. Question one: are you talking about a cold, unconditioned attic or an insulated sloping roof?

    2. Question two: do you prefer a ventilation gap or do you prefer an unventilated ("hot") roof?

  7. steve bumpus | | #7

    (1) insulated sloping roof
    (2) prefer unventilated (hot) roof

  8. GBA Editor
    Martin Holladay | | #8

    Steve,
    Insulated hot roofs are allowed in most building codes. In the 2009 IRC, for example, the requirements can be found in section R806.4.

  9. steve bumpus | | #9

    Thank you Martin!!!