Hi
Just trying to get opinion on thickness of Rim joist insulation should be? Zone 6
It’s new construction home. With 6″ exterior insulation everywhere but the rim joist because of a full wrap around porch, so there is a ledger board on the other side of the rim with blueskin VP 100 between the two on the OSB.
2-4″ then fluffy or 4-6″ then fluffy?
Any opinions appreciated
Thanks Dave,
The thickness is meaningless- code prescriptives are in R-value or U-factor. IRC code min R value for a basement band joist would be R19 where penetrated by joists, or R15 continuous insulation.
With no insulation on the exterior, in a zone 6 climate at least 35% of the total R needs to be air-impermeable insulation (50% is better) against the rim joist. Going with 2" of closed cell spray polyurethane (or well-sealed 2" cut'n'cobbled polyisocyanurate) and R13-R15 fluff on the interior side snugged up to the foam would work.
What are the R-values of the above grade wall?
Dave,
I'm with Dana. Focus on R-value and air sealing, not thickness. Here's a article on this topic that you will probably find helpful: https://www.finehomebuilding.com/2013/09/12/insulating-rim-joists
Why not insulate the porch side of the ledger board?
Thanks for the reply,
Yes sorry I should have said R- value
Dana, 2 layers of 3" polyiso outside and 2x4 studs with Roxul, roughly R40-44 depending on how you rate the polyiso.
I was thinking 4" closed cell which is around R20 - then 2x6 Roxul
Joel it would be to tough to flash it properly and each piece cut around the joist