Rim Joist Insulation Assembly with Exterior XPS
I know this question has been brought up before, but I’m not sure I’ve seen a conclusive answer on the best approach. I have 1″ of exterior XPS insulation. What is the most ideal method to insulate the interior side of the rim joist? Attached is a photos. I am thinking
Climate Zone 5a- -northern New Jersey
Option 1: Air seal interior joints at rim joist/sill/floor above and install 4″ of mineral wool batt insulation pushed against the interior side of the rim joist
Option 2: 1″ of EPS insulation cut and cobbled against the rim joist and 4″ of mineral wool batt pushed against the EPS
Option 3: ?
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Deleted
User ...783,
You need enough impermeable insulation (foam) to either keep the rim-joist, or the interior face of any foam you put in the inside of the rim-joists warm enough to prevent condensation.
For climate zone 5a, the R-value of the foam to do that is at least R-7.5. Since you don't have that amount on the outside you should go with option #2 to get to that R value.
Thank you!
I have the same question in another article...(https://www.greenbuildingadvisor.com/question/recommendations-on-this-basement-wall-rim-joist-detail).
For your 'Option 2' - Wouldn't 1" EPS on the inside be too little in thickness resulting in a cold interior condensing surface? And wouldn't this surface only be lowered in temp if 4" batt insulation is added?
I have 1" XPS on the outside too, and want to avoid a rim-joist-foam-vapor-barrier- sandwich, and allow drying if rim joist cavity gets wet... i also understand batt insulation alone causes issues due to its vapor/air permeance.
Bill had also recommended using EPS on the inside to allow for some inward drying, given that the exterior is likely impermeable XPS. But providing a minimum thickness may be the issue?
Maybe I am just overthinking it?
Thomas,
If there is already 1" of EPS on the exterior, adding an inch on the inside takes you above the R-7.5 necessary to keep the inside face of that foam warm enough to avoid condensation. That amount takes into account the 4" of batts. You don't end up with a vapour-barrier sandwich, as 1" of EPS is 2 to 5 perms
https://www.greenbuildingadvisor.com/article/calculating-the-minimum-thickness-of-rigid-foam-sheathing