Rigid foam + spray foam in unvented roof
![](https://secure.gravatar.com/avatar/41e8a5e4a6b019262d6c83731b8d376e?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fk.png&r=g)
I have an unvented cathedral ceiling (2×6 rafters) with open cell spray foam as cavity insulation. The 5.5” of foam only give me an R value of about 20. We are about to reroof the house and I would like to add rigid foam on the exterior side of the roof sheathing to increase the R value and also act as a thermal break. I’m in climate zone 2. R38 is required for ceilings.
My question is is this setup gonna work? I know you should not put rigid foam on the exterior when closed cell foam is used on the inside. I can’t find any info regarding open cell foam though. Am I correct in assuming that open cell foam is vapor permeable and I am therefore NOT creating a moisture trap?
Hi Quantum Girl,
You can add rigid foam insulation above your roof deck. The R-value you need to hit with the exterior insulation is not about reaching the code minimum R-value for a roof in your area, though. It's about having enough R-value on top of the deck to keep the sheathing warm and prevent condensation from occurring inside the assembly. I recommend that you read this article. It should answer your questions: How to Install Rigid Foam on Top of Roof Sheathing