Retrofit air barrier / WRB: Peel-and-stick vs. Solitex Mento 1000
I am in the process of renovating a 100-year old home in Manhattan, KS (climate zone 4/mixed humid). We are adding to the sheathing a WRB/Air Barrier membrane, 2″ of reclaimed polyiso foam, a 3/4″ rainscreen gap, and beveled Boral TruExterior siding.
I was planning on using a peel-and-stick roofing underlayment (a la PERSIST/REMOTE), but my contractor has expressed deep concerns about this approach curtailing drying in the wall assembly in our humid summers. He wants a vapor-open housewrap instead. It seems somewhat silly to me, as the polyiso is foil-faced and will be a nearly impermeable barrier, and the interior air will be conditioned promoting drying to the inside.
But the cost of using Solitex Mento 1000 vs. the peel-and-stick is almost a wash, after accounting for shipping and tape costs, so I would be willing to go either way. Are there any concerns about releasing water vapor under a layer of polyiso? Are any additional details required?
Thanks,
Nathan Bean
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Nathan,
Your analysis is correct. In Zone 4, you won't get into any moisture trouble if you install a vapor-impermeable layer on the interior side of 2 inches of polyiso. And, as you point out, if you are using foil-faced polyiso, you already have a vapor barrier at this location, with or without the peel-and-stick.