Regarding the November 2011 article on Synthetic Roofing Underlayments
![](https://secure.gravatar.com/avatar/c4d8e54f3af79ce071317339933e1d47?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
Should synthetic roofing underlayment be used on a roof with open cell foam sprayed against the roof deck with shingles in North Carolina? I sure hope so as we just did it with a house I am having built.
Chris,
According to manufacturers recommendations, almost all synthetic roofing underlayments can only be used over ventilated spaces (that is, vented cathedral ceilings or vented attics).
The only exceptions are vapor-permeable synthetic underlayments like Deck-Armor, Delta-Maxx Titan, VaproShield SlopeShield, Cosella-Dörken Vent S, Nemco Industries RoofAquaGuard BREA, or Cosella-Dörken Delta-Foxx. If you chose one of these vapor-permeable products, you probably know you did, because they cost an arm and a leg.
Your roof assembly is not ventilated, so if you used a typical brand of synthetic roofing underlayment, your installation violated the manufacturer's recommendations. It is also a code violation, since almost all building codes require all products to be installed according to manufacturer's recommendations.
So, you made a mistake. But now that the roof is built, I wouldn't lose much sleep, since it's too late to solve the problem. Your roof will probably work.
However, it you want to pursue a case against your builder, it certainly sounds as if your builder might have made a mistake.