4khz | Posted in General Questions on

I am proposing to reframe my garage roof per the attached sketch. My primary question: is a “ridge board” sufficient in this case ? 

Edit: typo on one measurement. The total length of garage is 34 feet, not 24 feet 

 

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    DCcontrarian | | #1

    There's really two questions with roof framing. The first is whether the rafters are big enough for their span. The second is how you keep the roof from spreading the walls.

    I don't see any provision for preventing spreading in your diagram. There's two ways to do it. One is to have a tie across the bottom of the rafters that draws them together. The other is to have a ridge beam. The ridge beam has to be supported at the ends by posts and capable of carrying half the weight of the roof.

  2. walta100 | | #2

    To my eye this question seems like only be answered by an engineer after a site visit.

    Walta

    1. 4khz | | #3

      I have an PE. He’s remote. There was some miscommunication. I wanted to get a third opinion (already got one from my framers). All sorted out. The sow per the sketch is ok.