Recommended insulation level in commercial buildings
What are the recommended R values for insulation in a commercial building that is conditioned? I am in Spencer, Iowa so that would be Zone 6.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Curtis,
You should contact your local building code official to determine the code requirements in your local area.
According to the 2006 IRC, residential buildings in Zone 6 need a minimum of R-49 ceiling insulation, R-20 wall insulation, and R-30 floor insulation. Whether the building is commercial or residential, I wouldn't recommend less insulation than the code minimum.
More is better.
The IECC standards are in Tables 802.2(1) through 802.2(7).
This link is to a DOE manual for inspections for the commercial provisions of the IECC: http://www.energycodes.gov/training/pdfs/iecc_com_wb.pdf
Look at the 2009 IECC, Chapter 5. Table 502.1 gives you the Building Envelope Uvalue for a particular building method (metal, metal framed or framed). Table 502.2 gives you the Rvalues for same. You should be familiar with the whole Chapter 5 as there are many other parameters and requirements for commercial buildings.
Curtis,
Ideally a developer thinks in terms of an energy goal and then determines the R-values, air tightness, window specs, and mechanical specs needed to meet that goal. PassivHaus principles are being applied to small to mid sized commercial buildings (office and school buildings) in Europe.