I’m trying to figure the best *if possible* way to install a recessed medicine cabinet on an exterior facing wall. Right now all I can think of is using 2×2 lumber to fir out my 2×6 wall, so that the medicine cabinet still allows 3.5″ of room for insulation behind it. (Assuming 3.5″ deep cabinet, and 2×6 + 2×2 = 7″ depth)
I would only use 2×2’s for the width of the vanity, and then return to standard 2×6 thickness so my linen cabinet would have the extra space, and the jog in the wall would not be noticeable with the cabinet fit in there.
I live in Zone 5, and am worried about the loss of insulation on top of the fact that the room is a humid environment. Would I be okay by using 3.5″ of rigid foamboard directly behind the box I build for the medicine cabinet, and then continuing my mineral wool in the rest of the wall cavities? With mineral wool I have to use the smart membrane, and wonder how I would detail this medicine cabinet “hole” compared to the standard studs? 3.5″ of XPS foam would not be vapor permeable, so I am concerned all the way around with my osb sheathing being able to dry if it needs to, while the wood in the cavity would only breath towards the medicine cabinet.
I'd go with the 2x2's.
If you have back-ventilated siding (say vinyl, or anything with at least 1/4" of rainscreen gap between the sheathing and siding) there shouldn't be a problem with stuffing 3-3.5" of foam behind the cabinet, sealing the foam to the OSB with a heavy bead of polyurethane caulk or foam-board construction adhesive to guarantee air never convects behind it, then sealing around it with can-foam.
If you go that route use rigid polyiso instead of XPS. Polyiso will be both higher performance (~R21 @ 3.5") and greener.
Nicholas,
Q. "Would I be okay by using 3.5 inches of rigid foamboard directly behind the box I build for the medicine cabinet, and then continuing my mineral wool in the rest of the wall cavities?"
A. It would be OK, except for the lower R-value.
If you want to have the full R-value of your wall insulation, consider installing a surface-mounted medicine cabinet. There are two advantages to this type of cabinet:
1. The mirror is closer to your face, and so it provides a better image (closer view) for shaving or makeup.
2. You don't have to reach as far to get the bottle of aspirin or Ibuprophen.
-- Martin Holladay