Range hood for whole-house ventilation?

dsmcn | Posted in GBA Pro Help on

Zone 4A. Whole house ventilation requirement is 67 CFM. Windows open 6 months/year during shoulder seasons. Range hood exhausts 250 CFM and is connected to a makeup air duct with damper (air is delivered through MERV filter to a central stairwell/atrium for maximum mixing). Q: could I not add a controller that turns the range hood on 1 hour six times/day?
Note: open floor plan so exhaust would draw from most of house.

If yes, can anyone suggest a controller for the range hood exhaust?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    David,
    I'm sure that you could implement your plan with an inexpensive 24-hour timer (available from any electrical supply house).

    I don't think it's a particularly good idea, however, for two reasons:

    1. Range hood fans are noisy.

    2. You'll be ventilating at a very high rate, followed by a period of time with no ventilation at all. This stop-and-go approach is more likely to lead to occupant complaints than using a quiet Panasonic exhaust fan, sized for your ventilation needs, operating for 24 hours a day.