Rain Screen Gap behind CI

SeanRyan | Posted in General Questions on

Hey All,

Was thinking I had my setup dialed for continuious exterior insulation:

Innie Windows:
– 2×6 wall with zip system sheathing
– Sealed at the sheathing layer with tape and fluid applied. This is water and air control layer
– 2″ Polyiso
– Batten for rain screen gap
– Siding

But, I was just looking around and saw a spec for a gap between the foam layer and the sheathing, in case any moisture gets back there.

Is this necessary? Is there a good way to add this in simply? The recommendation was for a drainable house wrap, but that feels really redundant over Zip.

Thanks,

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    MALCOLM TAYLOR | | #1

    Sean,

    My understanding from this https://buildingscience.com/documents/insights/bsi-038-mind-the-gap-eh is that it is only necessary if you have impermeable insulation and the sheathing has no way to dry to the interior. But maybe necesary is different that advisable?

  2. matthew25 | | #2

    If the gap between the exterior insulation and the sheathing is too big, wouldn’t it cause convection loops and possibly render the insulation less effective? I know Risinger put polyiso directly against his WRB on the sheathing but his assembly allows drying to the inside. He made a video where he poured red dyed liquid behind the polyiso and you can see it drain out the bottom, albeit taking a little longer than if it were an open rain screen.

    1. Expert Member
      MALCOLM TAYLOR | | #3

      Matthew,

      Joe Lstiburek qualified it in the article I linked to:
      " But won’t the tiny gap cause a loss of thermal performance of the foam sheathing? Yes. How much? About 5 percent of the thermal performance of the foam sheathing (not the entire wall assembly) with the 1/8-inch gap, less with a smaller gap."