Roof Assembly for Getting the Right R-Value
![](https://secure.gravatar.com/avatar/aadb98e9146a40fc9c73caaf7d04d3c1?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fm.png&r=g)
Hello,
We are adding offices in a warehouse in Southern California, and the architect is saying we need to have R-38 in the roof rafters. As far as I know R-38 batt is 12″ thick. The rafters are 2×4, 24 inches oc (please see image below). How do we go about putting up R-38 in this case?
To further complicate matters, we have also started putting up the offices (metal framing walls and ceilings, see attached image).
Thank you in advance!
Majid
Majid, the usual approaches would be to use spray foam in sufficient depth; furr down the framing with additional framing and fill the space with a fluffy insulation such as fiberglass batts; install rigid foam above the roof, which doubles as underlayment for the roof membrane. Your architect should be able to help you find the best option for your situation.