Poly under panelling ?

user-2360615 | Posted in Green Building Techniques on

I have a camp that I use mostly in the summer, but some in the fall/winter, that I have: insulated the floor, will spray foam the cathedral ceiling, rebuilt the walls with (outside – in) 19/32” T1-11 sheets (stained), 1 x 3 strapping (vented air space), Tyvek house wrap, 7/16 OSB, 2 x 6 studs, Roxul R24. And now I’m stuck. I have read many (most) of your articles, etc. on vapor barriers, permeability, etc., and if I understand correctly, I should not install a poly barrier, and go with primed and painted drywall, however, I would prefer for simplicity sake to go with 4×8 sheets of panelling. Any thoughts on how I could successfully keep moisture out of the wall cavity if I use panelling / other suggestions? Thanks.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    David,
    1. Where are you located? What is your climate zone?

    2. Vapor diffusion almost never causes moisture problems in walls. However, paying attention to airtightness is important. If you plan to install 4x8 sheets of paneling on the interior of your walls, make sure that you use a continuous bead of caulk or adhesive around the perimeter of each sheet when you install the paneling. It's also a good idea to use airtight electrical boxes.

    For more information, see these articles:

    Vapor Retarders and Vapor Barriers

    Forget Vapor Diffusion — Stop the Air Leaks!

    Do I Need a Vapor Retarder?

  2. user-2360615 | | #2

    Thanks for the quick reply Martin. I am a huge fan of your work.

    I am located in Ontario, Canada (in between Ottawa and Toronto) (Zone 6)

    I have installed poly vapor barrier boxes around each of the receptacles, and will seal them well. I presume I should caulk these to the panelling too.