Open-cell or closed-cell spray insulation in hot humid Bahamas roof?
We will spray insulate the underside of the plywood roof deck with at least R-20 foam. The attic encloses the A/C unit and ducts. The roof is reflective white shingles on Ice/Water membrane. One local installer says I should use an Open Cell (Icynene brand) insulation another says Closed Cell.
I will leave the insulation exposed in the attic apace.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Cynthia,
Either type of insulation will work. I would ask both installers how many inches (or centimeters) of insulation they plan to install. Open-cell foam has an R-value of about R-3.7 per inch, while closed-cell foam has an R-value of about R-6.0 or R-6.5 per inch. Choose the insulation with the highest R-value.
I don't know anything about building codes in the Bahamas, but in the U.S., exposed spray foam is considered a fire hazard. I would strongly suggest that you consider an application method that allows you to cover the cured foam with a layer of gypsum drywall.