Open-cell or closed-cell spray insulation in hot humid Bahamas roof?
![](https://secure.gravatar.com/avatar/f846b46ec31682481eea57a987b48936?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
We will spray insulate the underside of the plywood roof deck with at least R-20 foam. The attic encloses the A/C unit and ducts. The roof is reflective white shingles on Ice/Water membrane. One local installer says I should use an Open Cell (Icynene brand) insulation another says Closed Cell.
I will leave the insulation exposed in the attic apace.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
Cynthia,
Either type of insulation will work. I would ask both installers how many inches (or centimeters) of insulation they plan to install. Open-cell foam has an R-value of about R-3.7 per inch, while closed-cell foam has an R-value of about R-6.0 or R-6.5 per inch. Choose the insulation with the highest R-value.
I don't know anything about building codes in the Bahamas, but in the U.S., exposed spray foam is considered a fire hazard. I would strongly suggest that you consider an application method that allows you to cover the cured foam with a layer of gypsum drywall.