Need help with my detached garage roof assembly
Hi,
Our plans specify a detached garage connected to breezeway/screen porch, which is then connected to the house. I planned to stick frame the garage (2×4 @ 24″oc walls w/ 1″ exterior XPS). For the roof, I’ve got 2×6 rafters @ 24″oc, then 1/2″ plywood sheathing, then 30# felt, then standing seam steel roof panels. Should I add some rigid foam up there? Would that go above or below the plywood sheathing? Do I need to be concerned about venting?
Thanks
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Are you heating the garage? Where are you located?
No need to heat the garage, but don't want to freeze if we're out there for a while. I'm in Omaha, NE (zone 5).
Michael,
Most people don't insulate outbuildings that we not be heated or cooled with a space conditioning system.
Your comment -- that you "don't want to freeze if we're out there for a while" -- makes it clear that you are more worried about winter than summer.
Ceiling or roof insulation in an unheated garage will not make a garage any warmer. It might even make it colder, since the only two sources of heat for an unconditioned garage are the engine of a recently driven car (a minor source of heat) and the sun, which occasionally warms the roof (and therefore the interior, as long as there is no roof insulation) of a garage on sunny, snowless days during the winter.
Should I use a waterproof membrane instead of building felt or both?
Standing seam roofing IS a waterproof membrane, and is typically installed over #30 felt. Nothing more is needed or desirable.