I am in a bit of a panic and need some advice.

I am in the third year of building a large shop .. finally putting the roof on.  Just over 3000 sq ft on the bottom … 1200 sq ft of attic storage above.  I have put every nail in myself.

Standing seam metal over purlins.

Way back I asked the question, can I put metal over purlins.  I was assured by the supplier this was not an issue.   No moisture barrier of any type needed.   Just need good ventilation and insulation.

Installing purlins was a lot easier for me that 150 sheets of wood … plus it was cheaper so I could go with the standing seam roof rather than shingles.

Just a home shop so the moisture load is small (not like a horse barn).

Anyway … there is always dew on the roof … no issues.  Today for some reason, I reached under the roof as I was putting up panels … WET!

Now I know I don’t have any insulation in yet but you can not get more ventilation than completely open!

Concrete floor 20 ft below …. It has been there for 10 years  … no rain in the past two weeks.

I am not about to rip the roof off and put down sheets of wood … I have to work with what I have.

I will be insulating the ceiling.  The soffit and ridge are vented along the entire length.  There is at least a 6” air gap under the roofing.

Is there more I can do?

Spraying foam on the roofing is out of the budget .. plus the roof moves to I am not sure if that would work.

I could put something like Tyvek on the bottom of the top truss member to stop moister from going up.

I had planned on putting the insulation just on above the ceiling (as on the left side of the picture).  It would be a pain in the butt but I could put in closer to the roof to cut out the large air volume about the two shop wings (as in right side of picture).

Just trying to figure out where to go from here.

Here is a link to a short video I put up a few weeks ago … This side of the roof is now almost done.  There are more pictures and videos on my facebook page.

https://www.facebook.com/michael.csele/videos/900649032083441

Thanks …. Mike

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    MALCOLM TAYLOR | | #1

    Mike,

    Don't worry, it's entirely expected - and while it would have been a lot better to have a synthetic roof underlayment, it's not the end of the world.

    Poets taught us "dew falls", but it doesn't. Dew is moisture in the air condensing when it hits something cold. That can be the top or the bottom of the panels. Two things limit the amount on the bottom: The heat of the attic space (it's always warmer there than outside), and air-sealing the ceiling so the amount of moisture getting up there is reduced. Once you finish insulating and air-sealing the attic, the amount of condensation will be greatly reduced.

    1. xtal_01 | | #2

      Awesome ... that is what I was hoping. I left a 2 ft space ... ceiling to roof panel ... at the tightest point so I can get say 18" of insulation and still have a 6" air gap.

      Is there any benefit of moving the insulation in the "wings" toward the roof ... like in the blue on the picture rather than the red (right on the ceiling)?

      It is more work but I am thinking it might cut down the air volume in that unused attic area (above the side areas) and thus have less warm air?

      Thanks!

      1. Expert Member
        MALCOLM TAYLOR | | #3

        Mike,

        Warm air is good. The hotter those attics get the better. It will dry everything out and keep the roof panels hotter, which reduces condensation.

        Another advantage of leaving the insulation at the bottom of the trusses is the ease of air-sealing. Getting a good air-barrier where the insulation follows the roof-line is going to be difficult with all the truss webs interrupting it.

        1. xtal_01 | | #4

          Fantastic! Yes, it is much much easier to seal the bottom of the trusses.

          I have been super careful so far ... even calked in the plate to the pad.

          The pad is insulated and there is insulation down the outside of the pad and 24" outward.

          Definitely not a perfect building but if was relatively cheap to do and saves energy (money out of my pocket to heat) in the long run, I have done it.

          Thanks so much!

  2. Expert Member
    Michael Maines | | #5

    I am less optimistic about your situation than Malcolm is. That doesn't mean he's wrong, as every project is different, but I believe what you are seeing is condensation caused by night sky radiation. On clear nights, the roofing radiates heat directly to outer space, similar to how the sun radiates its warmth directly to our skin and other surfaces.

    Night sky radiation cools the roofing below the ambient air temperature, and if it drops below the dewpoint temperature of the air, moisture will condense from the air on both the top and bottom surfaces of the roofing. How much moisture is produced depends on many factors; it can be little, or it can be a lot.

    Most of the condensate that forms on the bottom side will find its way down the roofing and drip harmlessly, some will be absorbed and released by the purlins, and some will fall onto whatever is below the roofing.

    If you were to keep the roofing warm than you would eliminate the condensation, but if you have insulation in the roof then you almost certainly won't have enough heat loss to keep the roofing warm enough all of the time that condensation could occur.

    The two ways I address this are to include a watertight membrane below the purlins, or to install the roofing on sheet goods, which provides enough insulation to prevent condensation on the bottom of the roofing.

    In any case, I wouldn't panic but I would hold off on installing insulation until you have a better sense of when and where condensation is occurring. I bet it's worst on mornings after clear nights when the outdoor relative humidity is fairly high (aka when the air is close to the dewpoint temperature).

    If it seems like a significant amount, installing rigid foam between the purlins, and taping the seams so outdoor air can't reach the underside of the roofing, would almost certainly solve the problem.

    1. Expert Member
      MALCOLM TAYLOR | | #6

      Mike,

      I think it's mainly night sky radiance causing the roof panels to condense too. It's bad enough here in the PNW that the underside of our roofs sheathing often shows discoloration even in well built attics.

      I'm optimistic for two reasons:

      - Unlike the moisture accumulation you get due to air-leakage from the interior, night-sky radiance is sporadic, giving the roof time to dry out.
      - My experience has been that on metal roofs with purlins, even without an underlay, the moisture accumulation doesn't do much harm, as (much like walls) it's the sheathing that usually sees the damage.

      I would be more worried about a cathedral ceiling with those conditions that attics - which is another reason not to have the insulation follow the roof-line on this shop.

  3. xtal_01 | | #7

    I appreciate all the input!

    I was worried about this when I started looking at metal roofing.

    I put up a few posts about three years ago now. I kept getting reassurances that as long as I had good insulation and a good vapor barrier, there should be no problems.

    I am guessing everyone was thinking about the moisture from the building but not considering the moisture from the air gap I left.

    I am even thinking maybe a fan to vent the area on the days it detects moisture? I was told the idea is to keep a "cold roof" ... keep it the same temperature on both the top and bottom? Maybe a small fan would blow cold air into the attic area? Or as you said, do I want a warm area?

    Seems nothing is simple when building.