Modifying Existing ICF Walls
![](https://secure.gravatar.com/avatar/2541e893e50616f0bb031c7220c693ca?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fl.png&r=g)
We are considering purchasing a house built completely with ICF walls. Our purchase is predicated on being able to expand windows in two areas and lengthening a current window area to install french doors to a deck. The expansion of the windows would involve removing the wall between two windows and installing a wider three panel window.
Is this possible with ICF construction. If so what are the key things that must be considered in making these modifications.
Thanks
Ledicf,
Ideally, the rebar above each window is designed to handle the load and transfer it to the "jambs," just like a header in a wood-framed house.
If your walls have adequate rebar, you can make your window rough openings bigger with a concrete saw. If you need more rebar, you'll also have to remove concrete above the windows to pour what amounts to a bond beam. If in doubt, consult an engineer.
-- Martin Holladay
Martin,
Thanks a lot -- we were wondering about lintels -- your answer helps -- we would use an engineer and the original builder of the house to make any modifications.
The main issue will be creating a structural header over the new openings. ICF manufacturers sometimes have prescriptive guides for casting in reinforced concrete headers, but for various reasons you will likely need to use a solid steel header for the new span. You'll need to hire a structural engineer to size the steel header. If there is a high percentage of openings compared to solid wall, they may require additional wall reinforcement.
Edit to add: it's hard to pour a new header in place, and the rebar in a cast beam needs either a certain amount of development length on each side of the opening--enough to "bite" into the concrete--or specially designed hooks at each end. For a small opening it's nothing to worry about, but for longer spans it is. Solid steel--an "I" beam, C-channel or box channel--will be easier to retrofit. Architects like box channels but they are prone to condensation on the interior so it's better to use an open shape.