Mitsubishi R410a Correction Factors MUZ-FS06_18NA(H)
![](https://secure.gravatar.com/avatar/aef4c4561f9b32c9a1d29dc07b72c751?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Ft.png&r=g)
Good afternoon. I am part way through my Nitrogen pressure test. If it holds at 300 overnight I will proceed to the vacuum stage and then add R410a. I have a scale and all the proper tools.
I started with a 50 ft coil of line and I cut off exactly 56 1/2 inches leaving a remaining line length of 45.29 feet (45 feet 3½ inches). Any length of line above 25ft requires additional refrigerant. Thus, I need to run a correction factor. I read the Mitsubishi installation manual. The formula is below:
Calculation: X oz. = 1.08/5 oz./ft. × (Refrigerant piping length (ft.) – 25)
So, for 45.29 ft the calculation is such:
X oz. = 1.08/5 x (45.29 – 25)
X oz. = 1.08/5 x (20.29 ft)
X oz = 21.91 / 5
X 0z = 4.382
Does this look correct? The reason I ask is because I was watching a video on YouTube and maybe I misunderstood it, but it made it sound like I needed to add refrigerant for the total additional length added. In other words, I would need to add essentially double the above refrigerant because total line length is 45.29 for both legs – or about 90 feet total.
I think my instincts is correct and I just need to add the 4.382 ounces and call it a day. But I wanted to get other opinions.
Thanks!
Deleted
https://www.mitsubishitechinfo.ca/sites/default/files/SH_MUZ-FS06_18NA%28H%29_OBH873B.pdf page 11 labels the table as "Refrigerant piping length (one way)"
The example for 50' total (25' additional ) says 5.4 oz, so you're in the right neighborhood.
Thank you - I greatly appreciate your feedback. That's the table I have as well. I was 99% sure but wanted to get someone else's perspective since I'm doing this all in vacuum except for what I read and see online.
Pressure test held up overnight so I will likely be doing a vacuum today and add refrigerant. I may or may not do a triple vac. Section 4 (page 7 of 8) of the installation manual specifies a triple vac. I've been doing this by the book so far, so I may as well go all the way.
Thanks