Mitsubishi Outdoor Unit Modulation Range (and other specs)
![](https://secure.gravatar.com/avatar/f6e2de868751bf826bed516daec0f9b2?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
I’m looking to install a 1:1 minisplit in a renovated walk-out basement that is primary living space in zone 4A with a design day temp of 17. Architect and HVAC contractor’s current thinking is a Mitzubishi MLZ slim ceiling cassette. I see the hyperheat outdoor unit for this is the SUZ-KA09NAHZ. I’m concerned because the specs for this unit show a very small modulation range. Rated heat capacity is 12,000 btu/h, and minimum capacity is 8,000 (the cooling minimum is oddly better at 4,800). The non hyper-heat version shows a minimum of 4,000 btu/h. The MSZ high-wall head MSZ-FS09NA & MUZ-FS09NAH combo shows much better turndown with a minimum capacity of 1,600. On the flip side, the MUZ has much lower moisture-removal capacity than the SUZ( .6 pints/h vs 1.8).
Should I be concerned about the very limited heat modulation range of the hyperheat SUZ? It seems like it would end up being grossly oversized much of the heating season.
*Bump*
I'll bump again because I'm curious.
I notice the slim duct unit that also hooks to that ODU has similarly bad (at least on paper) min output. I am curious if those who advocate for ducted have any concerns with performance from a modulation standpoint.
Maybe the importance of low-end modulation has somehow been overblown, but from what I've gathered, it is important in those shoulder seasons and other low load days. So why opt for anything other than a 1:1 wall head if we're losing all that modulation capability?