Mitsubishi M series vs P series
![](https://secure.gravatar.com/avatar/687b06064411c1b598ffc196919ab490?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
I am coordinating construction of a new municipal garage in zone V.
The heating load is 36,000 btuh. The intent is to only heat the space to 50 degrees.
I understand the P series is more robust than the M series, but what does that mean in the real world?
Using two FH18’s to meet the load would seem to provide a significant improvement in the HSPF (7 to 9 in zone V). With that difference we could plan less solar PV to get to net zero. Thoughts? Thanks
Don't know the answer, but replying partly to bump, but also to ask: is the 36K heat loss at 50° or at 65-70° (eg "normal" temps)?
Also, the minimum heating temp on these is 50°. Whatever you decide, you should check the minimum output, so that they don't cycle excessively in the fall/spring.
The 36K heat loss was calculated at 68 deg. The building is now built and we did use M series.
Seems to be working fine.