Minimum Thickness of Timber HP on Exterior of 2×6 Walls

user-3813901 | Posted in Green Building Techniques on

Hey There, Fellow Tradespeople! 

I’m planning a wall system for a renovation project that will likely be (from inside out), 1/2” drywall, Intello Plus Smart Vapor Retarder, 2×6 studs with dense packed cellulose (between the studs), 1/2” cdx pine sheathing, WRB over cdx, a 3.5” layer of Timber HP Timberboard, ( R-13), over the WRB, 3/4” strapping (rainscreen) over the Timberboard, and wood clapboards—(R-33 total with R-13 continuous).

 

Does anyone know if the old rule of thumb for minimum required R-value for 2×6 walls, applies to Timberboard HP (wood fiber board)? I’m re-reading Martin’s article (and table) that specifies for Climate Zone 6, a minimum R-7.5 for 2×4 walls and R-11.25 for 2×6 walls, but believe this article was for foam sheathed walls–not wood fiber board exterior sheathing. 

 

What I’m hoping to find out, is if I can safely get away with a thinner layer of the Timber HP, to save money– like maybe the 2.5” thick (R-9) Timberboard, due to the robust inner vapor control layer, carefully detailed air tightness on the warm side, and “different than foam board” approach/ characteristics. Any takers on this one?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. gjmerz1064 | | #1
    1. user-3813901 | | #3

      Thanks! Interesting and a good start.

  2. Expert Member
    Akos | | #2

    Since the material is permeable, there is no minimum thickness. You can use as little of the material as you want as the sheathing can always dry to the exterior.

    If you go up to sufficient exterior insulation for condensation control (that R11.25) you can skip the interior vapor retarder. This is the case no matter what type of exterior insulation you have.

    1. user-3813901 | | #4

      Thanks for your input, Akos! I'll give it some thought and see what else I can find out. Appreciate your response!