Minimum requirement for roofing nails sticking through sheathing?

LoudMouth | Posted in Energy Efficiency and Durability on

Looking at a 2005 tile roof installation manual, it looks like the minimum penetration of a roofing nail into roof sheathing was 3/4″. So If I assume 1/2″ OSB sheathing, I should be able to cut the nails off with 1/4″ still sticking through the sheathing into the attic. Is this correct, or am I missing something?

Dave

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    ARMANDO COBO | | #1

    I’m sure your roofing manufacturer would have available downloads of their installation manuals. As I read a CertainTeed shingle installation manual (chapter 8), does not mention a word on cutting off any nails.
    "Nail shanks must be long enough to penetrate the roofing and then go ¾” into solid wood, plywood or non-veneer wood decking, or through the thickness of the decking, whichever is less.”

  2. GBA Editor
    Martin Holladay | | #2

    David,
    I disagree with your interpretation. Every time I read a requirement that says that 3/4 inch is "the minimum penetration of a roofing nail into roof sheathing," I interpret that to mean that the nail needs roof sheathing that is at least 3/4 inch thick, and that the nail must stick out the back side of the sheathing at least a tiny little bit.

    So, I think you need 3/4 inch plywood or solid board roof sheathing.

  3. user-741168 | | #3

    Some time ago (a hundred years?) roofing nails did not penetrate the deck. Thicker decks and shorter nails. I remember the difficulty twirling those 1" roofing nails. This had two benefits: 1) a neater looking attic, and 2) no condensing or frosting points. The downside, I think, is that the shrink-swell process in wood that "walks" the nail out of the deck can happen more easily.

    I've had historic jobs where I requested clipping the protruding nails with a bolt cutter.

  4. LoudMouth | | #4

    Just for clarification: The roof is done, and the 1/2" OSB assumption was a worst case. If the sheathing is actually 3/4", then I should be able to cut the nails off flush per the specification. The question was whether any cutting of the nails would cause a problem as long as I complied with the 3/4" in the original specification.

  5. GBA Editor
    Martin Holladay | | #5

    David,
    I'm confused. If the roof is done, you should be able to answer the question of whether the building has 1/2-inch roof sheathing or 3/4-inch roof sheathing.

  6. LoudMouth | | #6

    The question is whether cutting the nails will be a problem as long as I leave >=3/4" penetration after doing so.

  7. Expert Member
    ARMANDO COBO | | #7

    David,
    “When fasteners do not penetrate the deck at least 3/4” or all the way through thinner panels, the likelihood of nails backing out, or coming loose, is very high” Minimum nailing base should be 3/8” plywood or 7/16” OSB… If you are worried about condensation on the nails, then you should install a double-decker with rigid foam in the middle.
    What does your shingle manufacturer’s installation instructions say? What shingles are you installing?

  8. GBA Editor
    Martin Holladay | | #8

    Armando,
    If the manual calls for a "minimum penetration of a roofing nail into roof sheathing" of 3/4 inch, why do you write that "Minimum nailing base should be 3/8” plywood"?

  9. Expert Member
    ARMANDO COBO | | #9

    Martin,
    If you are using roof sheathing that is 3/4" or thicker, then the nail must penetrate 3/4" min. into the sheathing. If you are using an approved roof sheathing that is less than 3/4", like 7/16 OSB or 3/8" plywood, then the nail must go all the way through. They do specify the shank to be 11-12 gauge, the head diameter to be st least 3/8”, but no specs on how long the shaft needs to be after passes through a 7/16” or 3/8” sheathing.
    I do think it can be confusing the way their installation manual is written. I've contacted CertainTeed tech support and asked if they could answer this thread, hopefully they do.