Metal Roof SRI ratings
![](https://secure.gravatar.com/avatar/5730210db14ba879cf3601ecc4361563?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fp.png&r=g)
If a “cool roof” design has a SRI of 40 would going for a SRI of 54 make that much more of a difference?
Does having a cool roof help with the R-Value of roof assembly? According to the manufacturer they quote ORNL as saying it does help with summer time A/C loads, especially in high-desert climates.
Peter,
A "cool roof" saves energy when installed on a poorly designed home. It won't really save any energy when installed on a well-designed home.
The classic situation that might call for a "cool roof" is a hot-climate house with ductwork in an unconditioned attic. If you have such a house, you might consider installing a "cool roof."
If you follow GBA recommendations -- and all of your ductwork is located inside your home's conditioned envelope, and you have ceiling insulation that at least meets minimum code requirements -- you will see hardly any benefit from a cool roof.
As an addendum to Martin's correct answer, a cool roof also make a contribution to lowering the urban heat island effect. If you live in a hot climate urban area, using a cool roof is an important contribution to mitigation of that problem.
A cool roof also has the intended consequence of wintertime lower roof deck temps, which becomes a (very) modest increase in space heating load, but a more significant increase in high wintertime moisture accumulation in the roof decks for unvented insulated roof assemblies.
With very low pitch roofs there is still a cooling season energy use advantage to having a cool roof even at an IRC code minimums, but from 3:12 or higher that advantage fades very quickly. On large flat roof commercial buildings it's still "worth it", even in cold climates.
Would a cool roof with a high SRI help with RADIANT HEAT? For example, say there was a fire nearby and the heat from the flames creates radiant heat. Would a cool metal roof with a high SRI help to mitigate that radiant heat from penetrating into the roof sheathing/building?
The cool roof absorption/emissivity profiles are in the deep infra-red- the same spectrum as say, a forest fire. Only about half the solar spectrum energy is in the deep infra-red, the rest is in the visible and UV spectrum. Cool roof's work by re-radiating the deep infra-red back into the cold radiant-temp sky, while reflecting a good chunk of the near-infra-red, UV, & visible spectra.
So the short answer is, no, a cool roof with an SRI of only 10 won't reflect very much of the heat radiating from a nearby fire. It is not a low-E coating with broad infra-red reflectance- it is designed to be a deep infra-red absorber & emitter. A titanium-white high SRI finish would reflect a good portion of forest or house fire spectrum though.
But any metal roof has a lot to offer for keeping burning embers falling from that fire from igniting your roof!
http://www.intechopen.com/source/html/38093/media/image6.jpeg
http://science.nasa.gov/media/medialibrary/2000/09/05/sunspectrum_resources/spectrumgif.gif