Vapor Barrier: MemBrain or Paint
I’m getting ready to insulate the new workshop I built for myself – 44 ft x 30 ft with 12 ft tall ceiling. The slab is insulated with 2″ XPS under the entire slab, including the edges along with a 6 mil poly vapor barrier. The wall assembly is 2 x 6 studs, Tyvek, T1-11, Benjamin Moore latex primer, and Benjamin Moore Aura exterior paint.
The shop will be heated with a natural gas fired unit heater with a usual temp of 50 to 60 degrees in the winter, dropping down to 40 degrees when not in use for long periods of time (a week or more). There is a good possibility I may eventually add A/C at some point in the future. I live in SE Michigan, climate zone 5.
I will insulate the walls with 6″ of mineral wool and use the Air Tight Drywall method. My question is when it comes to a vapor barrier should I use a vapor barrier paint or MemBrain or nothing or ? Marty
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Use this when it comes to wall design and moisture. The temps of your use will mean that it is properly conservative (otherwise I'd use the Z6 values).
https://www.appliedbuildingtech.com/system/files/200311_abtg_rr_1701-01_moisture_control_guidelines_figure_update_final.pdf