Manual J and second floor heat loads

Jon_Lawrence | Posted in Mechanicals on

I am working through sizing a multi-split for a 2-story house and I have had both my engineer and my mechanical installer perform their own Manual J,D and S for the project. A large part of the 2nd floor is open to below and I am wondering if Manual J takes into account the heat gains coming from the 1st floor when determining the 2nd floor heat loads in a situation like this. Does anyone know if that is the case?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Dana Dorsett | | #1

    I don't believe Manual-J factors in interior convection or stratification exchanging heat between fully conditioned floors completely inside the thermal envelope of the building into account, only the losses from the conditioned room to the exterior. Modeling at that level is not really what the tool was designed for.

  2. Jon_Lawrence | | #2

    Excellent, thanks Dana.