Low-slope roof Climate Zone 6
![](https://secure.gravatar.com/avatar/85303c7fd83ace9bad549e257c32f74f?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fb.png&r=g)
Climate zone 6 entertaining roof options. Any concerns with performance or compliance of this assembly?
5/8″ Gypsum Board
3.5″ service cavity (with fiberglass R-13 Batts)
Intello membrane
14″ TJI sloped to 3/8:12 (with blown in fiber glass R-53)
1/2″ Advantech
Henry VP100 self adhered membrane
2 layers 3/4″ furring strips (one layer vertical, one horizontal)
1/2″ Advantech **
Peel and Stick roof membrane
For the wall assembly I decided on 3/4″ rainscreen, Henry VP100 self adhered membrane, 1/2″ Advantech, 2×6-2×4 double stud with blown in fiberglass R38, Intello membrane, 1/2″ Gypsum board
If the roof works the idea is tying the wall/roof membranes together similar to the “Perfect Wall House”
**I considered Densdeck but don’t know if it can be installed over furring strips or requires a solid underlayment.
I searched section 9 in the IRC but couldn’t find specifics. If I omit overhangs on the roof, is a parapet required?
Thanks,
Brandon,
No, that won't work. You can't vent a low-slope roof with this approach, because there will be no air flow through the ventilation cavity (even if you have soffit vents and a ridge vent -- and you didn't mention whether you were considering having those).
The only way to have a safe vented assembly with a low-slope roof is to follow the recommendations in this article: "Insulating Low-Slope Residential Roofs."