Is there a code requirement for residential boiler piping insulation?

Genmech | Posted in Building Code Questions on

Is there a code requirement for residential boiler piping insulation?

If so, what is the R-value for pipes in conditioned space? And unconditioned space?

We live near Baltimore, MD.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Brantley,
    According to Table 503.2.8 in the 2009 IRC, the minimum thickness of the pipe insulation is 1.5 inch for pipes with a diameter of 1.5 inch or less. Larger diameter pipe require thicker insulation, as shown in the table.

    Other code provisions require pipe insulation with a minimum R-value of R-3.

    No matter what these online resources say -- and no matter what advice I give you -- the final arbiter on these issues is your local code official. When in doubt, call up your local building office.