Is there a code requirement for residential boiler piping insulation?
Is there a code requirement for residential boiler piping insulation?
If so, what is the R-value for pipes in conditioned space? And unconditioned space?
We live near Baltimore, MD.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Brantley,
According to Table 503.2.8 in the 2009 IRC, the minimum thickness of the pipe insulation is 1.5 inch for pipes with a diameter of 1.5 inch or less. Larger diameter pipe require thicker insulation, as shown in the table.
Other code provisions require pipe insulation with a minimum R-value of R-3.
No matter what these online resources say -- and no matter what advice I give you -- the final arbiter on these issues is your local code official. When in doubt, call up your local building office.