My a-frame under construction is mostly roof. Is there any sort of insulation trade off that can be made to prevent me from having to do the entire 3200sf in minimum roof r-value (r-38 for north Georgia)?
GBA Detail Library
If you are on the IRC, you can reduce up to 500 sq.ft. or 20% of the ceiling area to R-30: https://codes.iccsafe.org/content/IRC2018/chapter-11-re-energy-efficiency#IRC2018_Pt04_Ch11_SecN1102.2.2, as long as you meet the criteria listed.