Insulation in a REMOTE wall cavity?

cbachand4772 | Posted in Green Building Techniques on

I am very interested in the PERSIST design but all i can seem to find when i search for details is REMOTE. I just saw a REMOTE wall detail in a jlc forum that included 2 x 4 wall framing and then fiberglass insulation in the cavity. Isn’t that going to lower the temp of your sheathing? kind of defeating the purpose of this type of construction? Also, I recently read a 2010 article by the CCHRC about a study done in 2002 in Alaska, and they found that the REMOTE style home they tested burned twice as much fuel as they had predicted. Would this be a result of not using the membrane on the roof? or is it possible that an oversized boiler, as they suggested, could be the reason? thanks in advance

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Chris,
    I assume you saw my article on the topic: Getting Insulation Out of Your Walls and Ceilings.

    Another resource is this Home Energy article by Chris Makepeace: "Wrap It Up: Building Houses with the Skin on the Outside."

    I agree with you that it's best to omit any insulation between the studs of a PERSIST wall. If you do end up putting insulation in the stud bays, be sure to do a dew-point analysis to be sure your sheathing won't get too cold.